Which circuit breaker to install? ABB B16 C or ABB B 20 C?

Alexander
1
answer
1066
views

Hello! The problem is this: in a new building from the electrical panel, a 3x4 wire is laid in the floor for a 220 V electric stove. There is one outlet. It is planned to connect the Shtil AT 220 / 100-1.0-50 step-down autotransformer, then there will be a 100-180 W amplifier + a 50 W turntable.

The question is which circuit breaker to install? At the moment, I noticed ABB B16 C and ABB B 20 C. Thank you in advance.

Visitors Comments
  1. Expert
    Vasily Borutsky
    Expert

    Good afternoon, Alexander.

    Of course, it’s better to ask a question to draw a diagram - a graphic image excludes interpretation.

    I understood from your question: a wire was sent from a 220 volt shield to an outlet. An electric stove and an autotransformer are connected to the outlet through a double / tee. The machine protecting the autotransformer is installed in front of the autotransformer, that is, after the tee / double.

    For further decipher the name of the autotransformer - AT-220-100-1-50:
    - AT - understandable;
    - 220 volts - primary voltage;
    - 100 volts - secondary;
    - 1 kVA - rated power transmitted by the transformer;
    - 50 hertz - AC frequency.

    The main parameter for you when choosing a circuit breaker is the transformer power of 1 kVA. Roughly speaking, you can assume that an autotransformer can supply electricity to a 1-kilowatt set of power receivers.

    The current flowing through the primary winding is determined as follows: 1000 watts / 220 volts = 4.5 A.

    Thus, you need any machine that cuts off the current greater than 4.5 A. The rating of "ABB B16 C" is too big, for "ABB B 20 C" even more. Any switch rated 4A is better, for example, "ABB S201M 1P 4A".

    If, nevertheless, you meant the protection of the wire “electrical panel - outlet”, then the machines that you “looked after” would also be suitable. Let me explain: for example, an aluminum cable AVVG 3 * 4, thrown through the air passes 30 amperes. Thrown in the floor will miss 20% less.