What to do if the pumping station does not stop when the desired pressure is reached?

Benjamin
1
answer
183
of viewing

Hello! Pump station does not stop, pressure as expected. Already replaced the pressure switch with a new one - it did not help. Replaced all that is possible ... But still, the pressure does not stop. How to be

Visitors Comments
  1. Expert
    Nikolay Fedorenko
    Expert

    If the reason that the station does not stop is not in the breakdown of the pressure switch, then the following should be checked, identified and corrected:

    1. Find the place of depressurization of the system (hidden leakage of water) and restore the tightness;
    2. Clean the reverse valve - maybe it is clogged;
    3. To get and clean the filter installed at the entrance to the station;
    4. Check if air is sucked in through the inlet pipe and exclude this possibility;
    5. Measure the value of the voltage supplied to the station and determine how stable it is - perhaps the reason is in the power supply;
    6. Get the ejector and check it for damage - it may be worth replacing it;
    7. The most incredible reason, but still happens sometimes, is a broken impeller that will have to be replaced.

    Give it a try. It is worth finding a malfunction and liquidating it, as the work of the pumping station will have to stabilize. If that - write, we will understand.

Pools

Pumps

Warming