How to connect the input and output of the heating pipe at the same level?

Anatoly
1
answer
229
views

Hello! Interested in one moment, is it possible to connect the input and output of the heating pipe at the same level? So that they are above or below the radiator. And why is such a connection not recommended? Thanks in advance for the answers.

Visitors Comments
  1. Expert
    Alexey Dedyulin
    Expert

    Good afternoon. Yes, it is possible to connect at the same level. All options and effectiveness are presented in two diagrams.

    Please note that there are new models of radiators that, when connected from the bottom, on the one hand, work as if with a diagonal. This was made possible by the installation of locking elements inside the batteries.

    You can also read about the connection and maximum heat transfer from radiators in this article on our website.